You are currently viewing our board as a guest which gives you limited access to view most discussions, articles and access our other FREE features. By joining our free community you will have access to searching the forum topics, post topics, communicate privately with other members (PM), respond to polls, upload your own photos and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

Both shore power circuit breakers went bad?

Discussion of batteries, chargers, wiring, generators, distribution panels, battery switches, etc.
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Both shore power circuit breakers went bad?

Postby dsolo » July 10th, 2017, 5:53 pm

Hooked up to shore power and had 110 v for a very brief moment. Now both breaker at shore power input bad? Turned off panel breakers to isolate power input and checked power cables, breakers. Breakers pass continuity check. But will not pass 110v. Breakers have no positive set. They have no resistance when throwing them on. What would cause this?? I have no ideas!
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders

User avatar

Canada
bud37
Admiral
Admiral
Posts: 4677
Joined: April 23rd, 2015, 10:22 pm
Has thanked: 547 times
Been thanked: 1143 times

Re: Both shore power circuit breakers went bad?

Postby bud37 » July 10th, 2017, 6:55 pm

Try this , you may have but.........shut down all 120 volts ac aboard boat , disconnect shore cables from the boat, check for power at the dock.....then try to reset each breaker at the shore power inlet, before you reconnect shore cords....
The above is strictly my opinion always based on years of doing...remember to support local business , it pays back.
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Both shore power circuit breakers went bad?

Postby dsolo » July 10th, 2017, 7:32 pm

Thanks for the advice. I tried the procedure several times. No luck.
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

United States of America
mjk1040
Admiral
Admiral
Posts: 1507
Joined: July 30th, 2015, 8:15 am
Vessel Info: 1998 355 AC/MY "Deja Vu"
Location: Savannah, NY
Has thanked: 9 times
Been thanked: 236 times

Re: Both shore power circuit breakers went bad?

Postby mjk1040 » July 10th, 2017, 7:58 pm

Well the moisture over time in that cabinet could have weakened them. Bet they were fun to get out and change in that cabinet. Could the gennset switch over failed and not switched back to shore input? Hope new one solve the problem for you.
Mike :down:
I'd Rather Be Boating!
1989 Sea Ray Seville
1986 Carver Mariner 32'
1990's Thompson 22' Cuddy Cabin
1990's 4Winns 245 Vista Cruiser
1980's Thompson 19' Open Bow
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Both shore power circuit breakers went bad?

Postby dsolo » July 10th, 2017, 8:07 pm

That could be the case. I had a tech working on the generator today. It is running and stopping quickly. He has a tech call into the tech support with the manufacturer.
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

Canada
bud37
Admiral
Admiral
Posts: 4677
Joined: April 23rd, 2015, 10:22 pm
Has thanked: 547 times
Been thanked: 1143 times

Re: Both shore power circuit breakers went bad?

Postby bud37 » July 10th, 2017, 8:16 pm

dsolo wrote:Source of the post That could be the case. I had a tech working on the generator today. It is running and stopping quickly. He has a tech call into the tech support with the manufacturer.

Well theres your problem, It was hard to believe both breakers would go bad at the same time.........open the breaker on the gen. itself and see if you can power up then.
The above is strictly my opinion always based on years of doing...remember to support local business , it pays back.
User avatar

United States of America
mjk1040
Admiral
Admiral
Posts: 1507
Joined: July 30th, 2015, 8:15 am
Vessel Info: 1998 355 AC/MY "Deja Vu"
Location: Savannah, NY
Has thanked: 9 times
Been thanked: 236 times

Re: Both shore power circuit breakers went bad?

Postby mjk1040 » July 10th, 2017, 8:22 pm

If the genset switch is the cause for a back feed, breakers may be toast. Or the switch not going back may cause a dead short or amp draw greater than the 30 amp shore cord breakers could handle. ??
Mike :down:
I'd Rather Be Boating!
1989 Sea Ray Seville
1986 Carver Mariner 32'
1990's Thompson 22' Cuddy Cabin
1990's 4Winns 245 Vista Cruiser
1980's Thompson 19' Open Bow

United States of America
tomschauer
CYO Supporter
CYO Supporter
Posts: 2290
Joined: March 28th, 2016, 10:52 pm
Vessel Info: 1998 Carver 355
Suspicious Fishes !
2022 Kawasaki 310X
Location: upper chesapeake bay
Has thanked: 313 times
Been thanked: 581 times

Re: Both shore power circuit breakers went bad?

Postby tomschauer » July 10th, 2017, 9:22 pm

If the genny back fed it should have toasted the breakers in the panel and not the ones at the shore power inlet.
It sounds like you have made certain you have 110 at the boat end of the cords and the wiring from the inlet plugs to the breakers are good?
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Both shore power circuit breakers went bad?

Postby dsolo » July 10th, 2017, 10:01 pm

Correct, I checked the voltage at the shore input and it had 120 vac. I then checked the breaker with a continuity tester and got continuity through the breaker. I connected the shore power and got 120 vac on the breaker input terminals. With breaker on there is no voltage at the breaker output.

Guys I need to know how these breakers fried? I don't want to replace them to only fry another batch.

I am in Leland township harbor. I discovered the toasted breakers here after connecting the shore power. I saw 120vac at the panel for a short time. It then went to zero voltage. The dock attendant stated the shore power I plugged into did not work? He switched the power source to a nearby terminal. It is the terminal I verified had 120 volts at the boat.

So I have two possibilities, Genny back feed, witch I eliminated the circuit by turning the generator breaker off. Made no difference.

Now, how could a bad voltage at the shore power terminal fry the boat breakers?

Dan
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders

United States of America
tomschauer
CYO Supporter
CYO Supporter
Posts: 2290
Joined: March 28th, 2016, 10:52 pm
Vessel Info: 1998 Carver 355
Suspicious Fishes !
2022 Kawasaki 310X
Location: upper chesapeake bay
Has thanked: 313 times
Been thanked: 581 times

Re: Both shore power circuit breakers went bad?

Postby tomschauer » July 10th, 2017, 10:28 pm

that's a tough one. Even if they screwed up and hooked you to the high leg of a delta system (about 170v) it shouldn't have toasted your breakers. It would have toasted everything else on the boat in fairly short order but not the breakers.