You are currently viewing our board as a guest which gives you limited access to view most discussions, articles and access our other FREE features. By joining our free community you will have access to searching the forum topics, post topics, communicate privately with other members (PM), respond to polls, upload your own photos and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

Kohler generator voltage drown when load applied

Discussion of batteries, chargers, wiring, generators, distribution panels, battery switches, etc.
User avatar

United States of America
g36
Admiral
Admiral
Posts: 1944
Joined: April 7th, 2014, 6:07 pm
Vessel Info: 1997 Carver 405
Location: Soddy Daisy TN.
Has thanked: 7 times
Been thanked: 587 times

Re: Kohler generator voltage drown when load applied

Postby g36 » August 10th, 2017, 8:32 pm

Its the service manual. If yours states owners it's not the same. Also the manual number on the front is TP 5414 look on the front of your manual and verify it's not the same it should be different if it's a owners manual.I'll also chrck my owners manual for the number.
1997 Carver 405
Crusader xli
The Black Pearl
Soddy Daisy Tn.

User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Kohler generator voltage drown when load applied

Postby dsolo » August 10th, 2017, 9:42 pm

Thank you g36. The tech has the manual, I will check with him.
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

United States of America
g36
Admiral
Admiral
Posts: 1944
Joined: April 7th, 2014, 6:07 pm
Vessel Info: 1997 Carver 405
Location: Soddy Daisy TN.
Has thanked: 7 times
Been thanked: 587 times

Re: Kohler generator voltage drown when load applied

Postby g36 » August 10th, 2017, 10:12 pm

i have the tp-5313 parts manual i can email if that would be of any help. im not sure if i am correct but i think we have a ford vsg 411/413 engine on the genset. i have that service manual i can email you too.
1997 Carver 405
Crusader xli
The Black Pearl
Soddy Daisy Tn.
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Kohler generator voltage drown when load applied

Postby dsolo » August 11th, 2017, 2:31 am

dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

United States of America
g36
Admiral
Admiral
Posts: 1944
Joined: April 7th, 2014, 6:07 pm
Vessel Info: 1997 Carver 405
Location: Soddy Daisy TN.
Has thanked: 7 times
Been thanked: 587 times

Re: Kohler generator voltage drown when load applied

Postby g36 » August 11th, 2017, 7:31 pm

dsolo check your email
1997 Carver 405
Crusader xli
The Black Pearl
Soddy Daisy Tn.
User avatar

United States of America
DanM
Deck Hand
Deck Hand
Posts: 91
Joined: February 8th, 2013, 5:49 pm
Vessel Info: Carver 396
Location: Lake Michigan
Has thanked: 5 times
Been thanked: 31 times

Re: Kohler generator voltage drown when load applied

Postby DanM » August 14th, 2017, 6:12 pm

dsolo,
I had this same issue with my 2004 10E Kohler in 2010. After much trouble shooting it turned out to be the Governor Controller Board. I made the mistake of purchasing it from an electrical supply house who said they were an authorized dealer but in reality was not supposed to sell it to an end user, and for good reason. It needs to be programed prior to installation and they didn't offer that service. After speaking with Total Energy Systems (not the organization I bought it from) they offered to program it for me. I had it back less than a week after I shipped it to them. It solved the issue and the generator has been running fine ever since. Total Energy really stepped up when they didn't have to. ---> :worthy: BTW they also had me clean and reset the flywheel pick up sensor. Even though it was not the issue they felt it should be done as a matter of course.
Dan

Carver 396
SugarSand Tango
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Kohler generator voltage drown when load applied

Postby dsolo » August 20th, 2017, 1:42 pm

Thanks for the information regarding the governor PCB. I am waiting to hear whether the mag-pickup is good. Marina had to order a 1K resistor, which took a week to get?? I also had to provide the test procedure to them. They know very little about Kohler gensets.

I suspect the governor PCB is bad. I should have results of the mag-pickup test Monday. I found a used PCB on eBay for $87. The seller can't garantee it, but will refund the$$ if found to not work. It is the original assembly and will not require programming.

I will take your recommendations on Total energy if needed. Are they listed on the website as a Kohler dealer?

Dan
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Kohler generator voltage drown when load applied

Postby dsolo » August 22nd, 2017, 10:50 am

Tested the speed pick up component. Applied 12 vdc with a 1K resistor in-line. Passed a metallic object across sensor and read open. No voltage at all. Net mag-pickup is $200 usd. Wish I knew the Honeywell part number, I am sure it is in the $30 range. You gotta love boating to put up with the price gouging.
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi
1997 Carver 405 MY
454 EFI Crusaders
User avatar

Topic author United States of America
dsolo
First Mate
First Mate
Posts: 193
Joined: October 24th, 2016, 2:56 am
Vessel Info: 1997 Carver 405 MY
454 EFI Crusaders
Name: La Belle ll
Location: Onekama, Michigan
Has thanked: 68 times
Been thanked: 25 times

Re: Kohler generator voltage drown when load applied

Postby dsolo » September 14th, 2017, 8:28 am

Just an update on the generator repair. Purchased the speed pick up from Kohler. Paid the $200 usd and waited a week for delivery. Fortunately the sensor was the problem. Up and running. Thanks for all the good input and manuals. Love this forum. Dan
dsolo
Vessel "LaBelle"
Portage Point Inn & Marina, Onekema, Mi