You are currently viewing our board as a guest which gives you limited access to view most discussions, articles and access our other FREE features. By joining our free community you will have access to searching the forum topics, post topics, communicate privately with other members (PM), respond to polls, upload your own photos and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

ac Freon refill

Anything related to the operation of your boat. Steering, Bilge Pumps, thru-hulls, bottom paint, etc.
User avatar

Topic author Canada
pepmyster
Admiral
Admiral
Posts: 972
Joined: June 5th, 2018, 7:17 am
Vessel Info: 2004 Carver 360 Sport Sedan
8.1 Volvo Penta
Fresh water boating
Location: Ottawa
Has thanked: 441 times
Been thanked: 190 times

Re: ac Freon refill

Postby pepmyster » July 26th, 2021, 2:51 pm

Ok, I'll go over this again this weekend before anything is done. I'll look again for restrictions of air flow. It's under the master bed in the forward berth.


United States of America
tomschauer
CYO Supporter
CYO Supporter
Posts: 2291
Joined: March 28th, 2016, 10:52 pm
Vessel Info: 1998 Carver 355
Suspicious Fishes !
2022 Kawasaki 310X
Location: upper chesapeake bay
Has thanked: 313 times
Been thanked: 583 times

Re: ac Freon refill

Postby tomschauer » July 26th, 2021, 2:53 pm

actually, when the coil starts to frost, it continues to reduce the air flow as the frost expands, thus making the problem worse, until you end up with a block of ice for a coil.
User avatar

Topic author Canada
pepmyster
Admiral
Admiral
Posts: 972
Joined: June 5th, 2018, 7:17 am
Vessel Info: 2004 Carver 360 Sport Sedan
8.1 Volvo Penta
Fresh water boating
Location: Ottawa
Has thanked: 441 times
Been thanked: 190 times

Re: ac Freon refill

Postby pepmyster » July 26th, 2021, 3:10 pm

Ya, then it leaks out , the water never see's the pan and leaks onto the carpet. ARGGGGGGGGG!!!!!
User avatar

United States of America
km1125
Admiral
Admiral
Posts: 3347
Joined: February 28th, 2017, 6:04 pm
Has thanked: 59 times
Been thanked: 969 times

Re: ac Freon refill

Postby km1125 » July 26th, 2021, 3:26 pm

pepmyster wrote:Source of the post Ok, I'll go over this again this weekend before anything is done. I'll look again for restrictions of air flow. It's under the master bed in the forward berth.

You have to look at both ends of the air distribution. There's typically ONE fan, and it has to do all the "pulling" and "pushing"
So it may not be air being blocked going INTO the evap, but air being restricted going OUT of the evap (to all the distribution registers). Any blockage or restriction BEFORE or AFTER the evap is suspect.

Also, If air is leaking around the evap, then it's not going THROUGH the evap, which is reducing flow there. The fan may still be blowing/sucking, but not actually all of it THROUGH the evap.
User avatar

United States of America
km1125
Admiral
Admiral
Posts: 3347
Joined: February 28th, 2017, 6:04 pm
Has thanked: 59 times
Been thanked: 969 times

Re: ac Freon refill

Postby km1125 » July 26th, 2021, 3:58 pm

tomschauer wrote:Source of the post actually, when the coil starts to frost, it continues to reduce the air flow as the frost expands, thus making the problem worse, until you end up with a block of ice for a coil.

This is true, but in all practical terms, you have to even get it down near freezing before it starts to frost up.

If you take a certain block of air (cu ft, room size, whatever) it contains a bit of moisture. Dropping that moisture in the room from 'room temp' (70, 80, 90?) down to below 40 takes 1 BTU per pound of water, or about 8 BTUs per each gallon. To just get that water to CONDENSE on the evap, even if it's still well above freezing (say, at 40 or 50F) takes ANOTHER 970 BTUs per lb of water, or 7,700 BTUs per gallon. Now, to get that to be freezing up on the evap takes YET ANOTHER 144 BTUs per lb, or 1,152 BTUs per gallon. None of that is actually factoring in actually cooling the AIR, but cooling the air is less of a challenge than cooling the water in the air, especially in humid environments.

So if you have a 12,000 BTU air conditioner, a substantial amount of that capacity is just sucking the water out of the air (which also effectively drops the air temperature, which is nice). But that also means that enough air flowing through the system will NEVER cause it to freeze up, nor get close to it.
User avatar

Topic author Canada
pepmyster
Admiral
Admiral
Posts: 972
Joined: June 5th, 2018, 7:17 am
Vessel Info: 2004 Carver 360 Sport Sedan
8.1 Volvo Penta
Fresh water boating
Location: Ottawa
Has thanked: 441 times
Been thanked: 190 times

Re: ac Freon refill

Postby pepmyster » August 9th, 2021, 6:21 am

So then, Went to the boat, got to the ac unit. Checked the coils, I used a mini shop vac that I have on the boat. Vacuumed the coils and made sure none of the fins were causing air flow problems. Then, I went to the shower sum pump, where the ac drains into. Put the vacuum on the line between the sump and the ac unit. Cleaned that out. I sure that was never done, I mean, who does that right? Anyway, I ran the unit for about 3 hours, no frosting or over spilling of water. All I'm hoping for is that this solved the problem, oh and yes, it's R22.

Return to “General Repairs & Maintenance”