My salon Marine Air 16,000 is tripping the breaker as soon as it kicks in. My A/C Pump is running and both my Forward and Aft units are functioning fine. I read somewhere that it could be the startup capacitor but I am not sure where to start with that. Is there any advice out there for troubleshooting this sort of problem?
Thanks in advance.
Bryan

Re: MarineAir 16,000 Capacitor

Posted: May 4th, 2020, 2:42 pm
by tomschauer
First check the resistance of the compressor windings. If any of the terminals C S or R have any reading to ground the compressor is shot. If that is the case, stop there and buy a new unit, not a compressor.