Re: '89 Santego, AC problem

Posted: November 9th, 2023, 10:18 am
by bobwhorn
The boat has been in TX quite a while so I have to assume the AC has been working. I think what happened is that the PO replaced the unit in the cabin with a larger unit, hence the pump issues. A bigger pump is on the list, but not at the top right now.
We'll see when I get gauges hooked up and add some Freon.

Re: '89 Santego, AC problem

Posted: November 9th, 2023, 10:42 am
by bud37
It will be interesting to see what size pump Ron is using. It seems to me I remember hearing GPH numbers for Oem pump installations in that BTU range having flow rates closer to 1000 Gph.

There was a thread about that a while back I believe. It has gotten warmer as of late, water and air.

Re: '89 Santego, AC problem

Posted: November 9th, 2023, 11:18 am
by km1125
What you can also do as a test.... turn off the other(working) AC unit and plug the water discharge. Then all the water from the pump will go through the salon unit. If it still has trouble cooling, then you KNOW the unit has a problem that needs to be fixed!! However, if you then get adequate cooling then you know you can solve your problem with a larger pump.

Doesn't cost you anything but time to do this, and the you have actual data to drive your decisions going forward.

Re: '89 Santego, AC problem

Posted: November 9th, 2023, 11:39 am
by Midnightsun
Dual 16,000 units would be borderline on a 500 gph pump IMHO. Midnight Sun has a 1000 gph factory unit pump with a total of 36,000 BTU split between 3 units. You have 32,000 BTU running on half the size pump. Prior experience with a single 16,000 btu unit on a new install required a 500 gph pump. The stronger the water flow, the more efficient your AC will become.

In other words, more is better in this case. I believe the minimal requirement is 200 gph / 12,000 btu however this is minimal and one must account for partial inlet filter clogs and loss of flow due to manifolds and elbows on multi unit applications. Go big.

Re: '89 Santego, AC problem

Posted: November 10th, 2023, 10:46 am
by bobwhorn
The PO apparently replaced the cabin unit with a bigger one and realized he now had a problem. He bought a 1000 gph pump, but air cooled, and it would overheat after a few minutes, so he went back to the 500 gph pump. He no longer responds to my text or email messages so this is an assumption.
I've been having to flush the line to the forward unit occasionally due to a high pressure shutdown. Now that the weather has cooled down we'll try to keep the system going as is, but planning on installing a bigger pump before next summer.

Re: '89 Santego, AC problem

Posted: November 11th, 2023, 11:17 am
by paulr
I am embarrassed to say I cant figure how to post on this forum but it seems there are a lot of you that know your air conditioners. I have a A/c problem as well on a 396 Carver froward AC and the mechanic said he couldn't' diagnose it because he could not locate the forward AC control box. When running just the froward AC the pump comes on and off intermittently. He found the pump relay in the forward bildge but not the control box. Can anyone help? Thanks

Re: '89 Santego, AC problem

Posted: November 11th, 2023, 1:20 pm
by bud37
paulr wrote:Source of the post
I am embarrassed to say I cant figure how to post on this forum

Choose the appropriate topic heading, at the top you will see New Topic, open that and go from there.